Viewing a single comment thread. View all comments

SomeConstructionGuy t1_j7uxb6t wrote

I agree the roi is long, but dollar per btu the spacepak is cheaper than propane and oil even at $.185/kWh down to about 0 in this setup. Aiming for short run times is directly contradictory to achieving high efficiency with a condensing boiler and high mass setup.

And it wasn’t my house, we just built it. But you couldn’t convince me to use a combi if it was free. I’ll always want an indirect with recirc

1

Optimized_Orangutan t1_j7uxrjh wrote

Absolutely, combis are the suckers bet. Indirect has some built in inefficiencies too because of losses across exchangers. An open system on the other hand, when done correctly, is superior to both. Most people don't know how to do an open system correctly though/are unjustifiably scared of it.

2

SomeConstructionGuy t1_j7uyoo1 wrote

Yeah it seems open system have been in the realm of diy for a long time in our area. The problems aren’t a result of open systems themselves but of unqualified design and install. That’s given them a bad rap.

2